Basic Managed Network Requirements
Basic managed network requirements are valid for any Eos network system which will be permanently installed, or those utilizing any of the following:
Basic managed networks are most Eos Family networks, including all permanently-installed networks, specifically utilizing any of the following:
  • 5–25 Eos Family devices in any Multi-Console Sessions.
  • 12k–75k outputs (24–150 universes) of sACN and Art-Net cumulatively.
  • 11–100 network endpoint devices (gateways, dimmer racks, fixtures, etc.)
  • Basic show control, with input via gateways into the entertainment control LAN, or via dedicated NIC input on console devices. No routed show control.
Networked Eos systems have specific hardware and software requirements which are detailed in this section. See the Guide to ETC Network Requirements for general requirements for ETC network systems.
CAUTION: These requirements are tested by ETC. Other network configurations may function, but are not supported. Requirements must be met specifically and explicitly for ETC to support a system. Equipment that is lacking information, from third-party manufacturers or otherwise, is considered to not meet requirements. If these requirements are not met, your system may not work as expected or desired, and ETC may not be able to resolve related issues until the system infrastructure is corrected.
Physical Infrastructure
Cabling and Communication
Hardwired infrastructure is required for all ETC hardware, which primarily utilizes RJ-45 connectors.
All cables must be marked on the cable jacket as meeting or exceeding the listed standards.
  • All cabling used for 1 Gbps connections must meet or exceed:
    • 1000-Base-T communication standards (IEEE-802.3ab)
    • Category 5e cable standards (ANSI/TIA 568.2-D)
  • All cabling used for 10 Gbps connections must meet or exceed:
    • 10G-Base-T communication standards (IEEE-802.3an)
    • Category 6a cable standards (ANSI/TIA 568-C.2)
SFP-connected cable and fiber requirements are determined by the installed transceiver. The following supported transceivers can be installed in Eos Family hardware.
Description Connector
Type
Supported
Speeds
Product
Code
Supplier
Part Number
Intel Ethernet SFP+ SR Optical Module, Dual Rate 1000BASE-SX 1GbE and 10GBASE-SR 10GbE SR 1 Gb
10 Gb
E10GSFPSR FTLX8571D3BCV-IT
AFBR-703SDZ-IN2
FTLX8571D3BCVIT1
FTLX8574D3BCV-IT
AFBR-709DMZ-IN2
AFBR-709DMZ-IN3
E10GSFPSRG1P5 FTLX8571D3BCV-13
FTLX8571D3BCVI31
FTLX8574D3BCV-I3
FTLX8574D3BCV-I5
E10GSFPSRG2P5 AFBR-709DMZ-IN7
AFBR-710DMZ-IN2
Intel Ethernet SFP+ Twinaxial Cables, 10GbE/1GbE Direct Attach passive Copper cable RJ45 10 Gb XDACBL1M PSF1PXA1MBLLN
NDCCDA-I201
XDACBL3M PSF1PXA3MBLLN
NDCCDA-I202
XDACBL5M PSF1PXD5MBLLN
NDCCDD-I202
603830005
Intel Ethernet SFP+ LR Optical Module, Dual Rate 1000BASE-SX 1GbE and 10GBASE-SR 10GbE LR 1 Gb
10 Gb
E10GSFPLR FTLX1471D3BCV-I3
FTLX1471D3BCVI31
Intel Ethernet SFP+ Optics - SRX (Extended Temp), Single Rate 10GBASE-SR 10GbE SR Extended Temp 10 Gb E10GSFPSRX FTLX8574D3BNL-IT
The following connections (including installed, portable, and patch cables) must meet or exceed the listed communication standards.
  • All switch ports connecting to Eos Family and ETCnomad devices must communicate with 1000-Base-T or higher standards. 10G-Base-T is preferred.
  • All switch ports connecting to other switches must communicate with 10G-Base-T or higher standards.
  • All switch ports connecting to network endpoint devices (gateways, dimmer racks, fixtures, etc.) must communicate with 100-Base-T or higher standards.
Many endpoint devices are not gigabit capable. Your cable and switch should be capable of carrying appropriate data speeds, generally 100-Base-T or 1000-Base-T. Consult the documentation for any network devices to determine the necessary speeds.
For the purposes of entertainment networking, a delay of 500 ns (0.5 μs) per 100 m (328 ft) segment is sufficient to include when calculating latency for all cable types. For more information, see Eos Network Overview > Network Wiring > Cable Latency.
It is recommended that all network ports be capable of providing Power Over Ethernet (PoE) with the ability to enable and disable on a port-by-port basis. ETC hardware implements 802.3af/at unless otherwise specified.
Topologies
See Eos Network Overview > Network Topology for general information about network topologies.
Single-switch networks must meet the following requirements.
  • The network switch must comply with all other network requirements.
Multi-switch networks must meet the following requirements.
  • Star-topologies only, with no loops, and minimized branches.
  • A network supporting Eos Family sessions shall not exceed 6 hops along the furthest path in the network.
Switches
Port Bandwidth
  • All switch ports connecting to Eos Family and ETCnomad devices must support connections of at least 1 Gbps.
  • All switch ports connecting to other switches must support connections of at least 1 Gbps.
  • All switch ports connecting to network endpoint devices (gateways, dimmer racks, fixtures, etc.) must support both gigabit and megabit connections, as many endpoint devices are not gigabit capable.
  • All network ports must auto-negotiate 10/100/1000 Mbps speeds. The ability to set static speed on a port-by-port basis is preferred. Select hardware provided by ETC operates at lower speeds of 10/100.
  • Throttling (static or dynamic) of network bandwidth is not permitted.
Switch Bandwidth
Full-bandwidth switches are recommended for all systems, particularly larger systems that are approaching the limits of a basic managed Eos network.
  • Switch bandwidth must be no less than 60% of the capacity of the total possible bandwidth of all ports.
To calculate switch bandwidth, see Eos Network Overview > Network Switches > Switch Bandwidth.
Switch Latency
  • Switch latency shall not exceed 125 microseconds (μs).
  • Full network latency, which includes all downstream switches, shall not exceed 22 milliseconds (ms).
Switch Configuration
Switch configuration issues can be as detrimental to a network as poor cabling, too much traffic, and so on. Smaller systems may be able to minimize these problems with an unmanaged network; see Unmanaged Network Requirements.
Internet Group Management Protocol (IGMP)
Internet Group Management Protocol (IGMP) must be supported and enabled on all switches in the system.
CAUTION: Adding switches to a system that are unmanaged or have misconfigured IGMP settings can cause issues with multicast traffic and violates network requirements. IGMP settings must match across all switches. ETC recommends using switches of the same brand, model, and firmware version throughout your system.
  • All switches and connected devices in a system must use the same IGMP version.
    • Mixing versions is not supported. While IGMP v3 is backwards-compatible, v2 is not compatible with v3. Eos uses IGMP v2.
  • IGMP snooping must be enabled on all switches.
  • IGMP querier must be enabled on all switches, and all settings must match.
    • Querier must support devices utilizing IGMP v1, v2, and v3.
    • Robustness must be set to 2.
    • Interval must be set to 30.
  • All switches must offer a minimum of 150 IGMP groups. ETC recommends 300 groups or more.
  • IGMP packet forwarding must be enabled on all switches.
  • The network shall support simultaneous IGMP join requests per device.
Rapid Spanning Tree Protocol (RSTP)
Other Switch Features
The following features and their settings are exceedingly specific to individual network configurations and can cause severe disruptions in entertainment control networks if misconfigured. As such, ETC does not have any recommended settings for these features and does not offer support for systems where they are utilized.
External and Wireless Connections
Other Devices and the Internet
ETC lighting systems have traditionally used isolated networks with dedicated network hardware and cabling that are physically separate from corporate intranets and the outside world. This is the required network arrangement for advanced and basic managed networks and remains the best practice for all networks regardless of size and complexity.
Systems where network infrastructure must be shared must follow Advanced Managed Network Requirements.
  • Facility intranet(s) and the ETC entertainment control network shall be separated physically (preferred) or logically (VLAN).
  • The greater internet shall not be routed to or from the ETC entertainment control network.
Show Control
Network-based show control must meet the following requirements:
  • ETC Show Control Gateways may be connected directly to the entertainment control network.
  • Other show control sources must be connected to Eos Host devices directly via secondary network ports (NICs).
    • IP Addresses for the secondary ports must be in a separate subnet from the entertainment control network, and may be assigned statically or using DHCP.
    • Show control sent to a specific IP address should target the addresses of the secondary ports of both Host devices.
  • Control Protocols show control must be connected individually to each Eos device that requires it.
Wireless
  • Wireless networking is only permitted for use with approved and supported ETC software applications.
Use of Wireless Networking hardware is subject to the following requirements:
  • Wireless connections to the entertainment control network are only to be used for Wi-Fi remotes.
  • Wireless connections between Eos devices are not supported.
Wireless Access Points are preferred in entertainment control networks. Routers are not recommended due to their relative complexity to configure and higher potential of delaying or blocking real-time lighting data.
Protocols and Services
The following protocols and services must be supported.
Internet Protocol
Use of Internet Protocol (IP) is subject to the following requirements:
  • ETC prefers that all ETC devices use static IP addresses in a single IPv4 subnet (/16 preferred).
    • ETC default IPv4 scheme is 10.101.0.0/16.
  • Limitations on the quantity of active MAC addresses per network port is to be coordinated prior to an ETC technician’s arrival.
  • All IP addresses shall be private. No public IP address is required as the ETC lighting network shall not be on the internet. For more information about private IP ranges, see Address Ranges.
IPv6 addressing is not currently implemented in ETC hardware.
sACN and Art-Net
Use of Streaming ACN (sACN) and Art-Net is subject to the following requirements:
  • Multicast shall not be restricted, filtered, or blocked.
  • Multicast address ranges used by ETC are part of industry accepted standards and protocols and are non-negotiable. They cannot be modified.
    • A list of multicast address ranges used by ETC is available upon request.
  • Anycast communication is not supported by ETC product.
  • Jumbo frames shall be allowed/permitted.
Network Time Protocols
Use of Network Time Protocol (NTP) and Simple Network Time Protocol (SNTP) is subject to general networking requirements.
