  • Remote Interface Unit (RIU) and Remote Video Interface (RVI) Jumpers and Dipswitch Guide
    REMOTE INTERFACE NODE PCB [4052B5014]
        Switches are either On (Closed) or Off (Open).
        The Remote Interface does not use DIP switches 7 or 8 .
        DIP switch 1 must be Off and 2 must be On or the Remote Interface will not   start.
    Main DIP Switch Function (S1)
    1Factory Use OnlyOff (Open) Normal operation
    2Factory Use Only
    On (Closed) Normal operation
    3,4,5,6DMX512 Addressing
    Off, Off, Off, OffPorts 1-3 (1-1536)
    Off, Off, Off, OnPorts 4-6 (1537-3072)
    On, On, On, OffPorts 7-9 (3073-4608)*
    7UnusedOff (Open) Normal operation
    8Unused
    *4600 DMX Outputs only supported with Obsession II systems
    Network Jumpers for Rev A PCB (J22)
       Locate jumpers 1 through 14.
    BNC (Thin-Net) connections
       Install jumpers 1 through 6
       Jumpers 7 through 12 are not installed.
    RJ45 (UTP-Twisted Pair) or DB15 (ThickNet) connections
       Install jumpers 7 through 12
       Jumpers 1 through 6 are not installed.
       Jumper 14 should always be on. Jumper 13 must always be Off.
    Network Jumpers for Rev 0 PCB (J22)
       Install jumpers 9 through 14
       Jumpers 3 through 8 are not installed.
       Install only jumpers 3 through 8
       Jumpers 9 through 14 are not installed.
       Jumper 1 must always be On. Jumper 2 must always be Off.
    Check Power Supply Voltage
       Verify that the Node Card is getting proper DC voltage by metering between TP1 and Com.  You should get 5.05vdc between these two points. If not adjust voltage at the       power supply so that you get 5.05vdc between TP1 and Com.
    REMOTE VIDEO INTERFACE--PROCESSOR PCB [4053B5001]
    1Factory Use OnlyOn (Closed) Normal operation
    2 - 5Factory Use OnlyOff (Open) Unused
    6,7Factory Use OnlyOn (Closed) Normal operation
    8Factory Use OnlyOff (Open) Unused
    Network Dipswitch settings for Rev A and Rev 0 PCB
       Locate the two sets of DIP switches, visible through the right side panel of the RVI.
       Set the back six DIP switches to On (up)
       Set the front six to Off (down).
    RJ45 (Twisted Pair) connector or the DB15 (ThickNet) connector
       Set the front six switches to On (up)
       Set the back six to Off (down).