  • SmartBar2 or SmartModule2 Dimmers Do Not Dim
    Question:
    My 6 Channel 3-Phase SmartBar2 or SmartModule2 circuits just turn all the way on or off with no dimming. I already checked the menu on the bar or module and the dimmer curve is set to linear.
    Cause:
    Please check the power feed to your SmartBar and SmartModule. A 6 channel SmartBar or SmartModule requires 3-phase power and needs to be fed by a single 3-pole breaker to guarentee proper operation. If your unit is being fed by 3 individually breakered circuits, this will need to be resolved by an electrician. There are a few reasons for utilizing the 3-pole breaker.
    The first is the most important: this is a safety issue.  The National Electrical Code dictates that when supplying power to 3-phase devices, a single 3-pole breaker must be utilized.   In everyday terms: imagine needing to service the unit and turning power off to the Smart product.  If the supply voltage is fed through a single breaker (a single 3-pole breaker, in this case) you can be confident all power has been shut off and it is safe to proceed.  If the unit is fed from 3 individual breakers, an unsuspecting colleague could "shut off the power" by switching a single circuit breaker.  Most people are used to this convention.  It is the same with your dryer or stove--a single breaker that you switch--not multiple breakers located in separate locations on the panel.
    Now as for the SmartBar or SmartModule not dimming properly, there are issues caused by using 3 individually breakered supplies.  Unless the 3 breakers are all turned on simultaneously, the SmartBar will not have a chance to compare the sine waves from all feeds to determine the proper operating parameters.  This will adversely affect the dimming.
    Additionally, the power cable for the 3-phase SmartBars and SmartModules has conductors sized for three phase operation.  If wiring into three separate circuits that aren't all on differing phases of the same feed, it is possible to overload the current carrying capacity of the neutral conductor causing the wire to heat up and possibly fail.
    If you have any questions regarding this topic, please feel free to call ETC Technical Support at 800-688-4116.
