  • ELV Modules And Test Mode In Sensor CEM+ & CEM3 & DRd
    This information is accurate as of 7/29/11.
    Going back to the first release of Sensor/Unison ELV modules, there has been a lot of discussion about their function with a rack in test mode.  After some investigation, here are the facts as we currently know them:
    CEM+/CEM3
    The ELV module circuit must be powered (with the breaker on) before getting a control signal in order for the module to output.
    Why?
    The processor in the ELV module needs to see a zero on the pwm line before it is ready to output. With CEM+/3, test mode supplies a constant +5V signal starting before the module boots so the ELV never starts outputting.
    Ramification
    In a Sensor+/3 rack in test mode, it is possible for a working ELV module to have signal LEDs illuminated with no fault indication and still not output.
    • Breaker trip/reset on a previously working circuit in test mode
      • Rack running in test mode
        • ELV module signal LEDs on and output circuit on.
      • Turn module breaker off
        • Signal LEDs stay on, output circuit off.
      • Turn module breaker back on
        • Signal LEDs stay on, output circuit stays off.
          Note: This will only occur in test mode. In normal or set levels operation, the pwm signal will be turned off for zero cross blanking time during every half-cycle and the ELV will output after its breaker is reset.
    • Rack power applied with test mode active (a.k.a. How an EC may turn on lights during installation)
      • Power on rack with CEM+/3 installed in test mode
        • ELV signal LEDs on, output circuit off.
      • Loosen the CEM+/3 from the backplane and reseat.
        • ELV signal LEDS on, output circuit on.
    Caution: Do not remove the CEM+/3 from the rack. To maintain arc flash protection, keep the module within the rack -- only unseat/reseat it from/into the backplane.
    DRd
    DRd uses zero cross blanking time even in test mode. Consequently, an ELV should turn on even after a breaker trip/reset. However, there is a software bug that may inhibit test mode function in some versions of DRd code.
    • In DRd dimming engine versions 1.0.2 and below and 1.2.0 and above, a slot configured for an ELV module will turn on in test mode.
      • Affected
        • PACP 2.0.1+; 1.0.0-1.1.2 (but not 1.1.2b)
        • SACP 1.2.0+; 1.0.0-1.0.1
    • In DRd dimming engine versions after 1.0.2
      • A slot configured for an ELV will not turn on in test mode.
      • An ELV module in a slot inaccurately configured as a standard (Dxx) dimmer module will turn on in test mode.
      • Affected
        • PACP 1.1.2b-1.2.2
        • SACP 1.1.0-1.1.4
      In Brief: The ELV will fire with CEM+/CEM3 test mode IF these steps are followed:
      1. Insert the dimmer into the rack and turn on the dimmer circuit breakers.
      2. Put the CEM+/3 into test mode.
      3. Insert the CEM+/3 in the rack and/or energize the rack.
      Basically, if you provide power to the ELV10 before the CEM+/3, the ELV10 will not fire.