Question: When I press the button for a preset that is already activated, it activates the off preset. How do I disable that? Answer: Under a station's property's uncheck the box that says: "Enable Off Toggle."
-
Question: In a 2 rack Unison dimming system with a CMEd and CMd how is data sent from the stations to a second unsion rack? Answer: Station data is taken in by the CMEd in the first rack. The CMEd processes the info and sends DMX out to the second rack.
-
SEE ATTACHMENT: 7180.Loading a Unison Config.doc
-
Question: Why do some lights stay stuck on when Unison Reboots? Answer: This is a hard question to answer as one sites failure is another sites desired functionality. Let me try to explain what occurs when Unison is rebooted so you can understand what is happening and why there are some cases where lights...
-
How loud is a Unison dimming rack? During the development of the Unison Paradigm/SmartLink DRd dimming rack ETC performed some rudimentary testing of the noise output levels of both a Unison Legacy DR dimming rack and a Unison Paradigm/SmartLink DRd dimming rack. The testing was done in a stairwell with...
-
With the introduction of the Unison Heritage and Unison SmartLink Heritage architectural control stations, ETC aligned our faceplate coloring with the RAL color standards. Model # Suffix Color Name RAL Color -1 Cream RAL 9001 -2 Ivory RAL 1015 -3 Gray RAL 7001 -4 Black RAL 9004 -5 Signal White RAL 9003
-
Many ETC products provide timed event capabilities and may be affected by the 2007 adjustments to US Daylight Saving Time enacted with the Energy Policy Act of 2005. See the ETC Daylight Saving reference page for more information on what steps to take with your individual product
-
The legacy Unison remote and Unison Heritage remote are the same hardware, however some changes were made to the remote and button placement that will affect their functionality. Both remotes are compatible with Legacy Unison hardware, however the Heritage remote must be used for Unison Paradigm systems...
-
We often get asked about wire temperature ratings and how they relate to dimmer rack wiring and the allowable number of circuits in a conduit or wireway. While the ultimate authority on wire size, temperature ratings, and conduit fill is the project electrical engineer, and then the local inspector,...
-
If your relays are chattering or not firing in your Sensor, Sensor+ or Unison rack there may be a problem with the neutral wire on your signal distro card. Make sure that the neutral wire is present and connected on both ends. This problem can also cause ELV10 modules to not work correctly in test mode...