Verify that the Max Scale setting for each dimmer on the CEM+ is set to about 118. Verify that the Curve setting for each dimmer on the CEM+ is set to Mod Square. If this doesn’t work, try Sensor 2.0. Make sure to check the voltage readings with a True-RMS meter. NOTE: Any work (including metering...
-
There are three fuses labeled F3-5. F3 and F4 are 1/8 Amp, F5 is 1.5 Amp F3 is C phase detect F4 is B phase detect F5 is A phase detect and supplies power to the MPE and the fan.
-
Manuals Sensor Rack User Manual- MPE Control MPE- DMX 512 Related Links: Dimmer Doubling Knowledge Base: How do I Reset an MPE? Sensor MPE DIP Switches Sensor MPE Self-Tests MPE Fuses How do I match intensities and dimmer curves between an MPE or Sensor CEM and a CEM plus processor? MPE DMX Problem Help...
-
Question: How do I know if my MPE is receiving DMX properly? Answer: If the LED labeled DMX is on solid, it is receiving DMX. The LED blinks if there is a communication problem.
-
When equipment goes bad out in the field, it's often extremely helpful if the owner/end user can keep track of the circumstances of the failure. This is especially true when the problem is intermittent and might not occur when the technician is present. Service Technicians are exceptionally skillful...
Posted to
ETC Product Wiki
by
Kelsey Aleckson
on
08-24-2009
Filed under: AAS, Acclaim, arri, ASTS, AVAB, CEM, CEM+, Congo, CongoJr, cRRFU, DAS, Dimmer, Distribution, DMX, ECMUX, Element, ELTS, Emphasis, Eos, ETCLink, Ethernet, Express, Expression, GCE, Idea, Ion, Irideon, K96, KnowledgeBase, Legacy Unison, LMI, Lon, MDD, MDR, MicroII, MicroVision, MIDI, MPE, NCE, Net2, Net3, Obsession, ObsessionII, Pharos, RDM, Response, RFR, RFU, RRFU, RS-232, RVI, Sensor, Sensor+, SineWave, SmartBar, SmartFade, SmartFadeML, SmartModule, SMPTE, Source Four, Source4, Touchscreen, Unison, Vision, WRFU
-
There is a recessed button on the face panel labeled RESET. Press and release it.
-
DIPs 1,2,3 set rack size / type Configured as: DIP1 DIP2 DIP3 SR6 3x12k Off Off Off SR6 6x6k Off Off On SR6 12x2k Off On Off SR12 6x12k bal. Off On On SR12 12x6k bal. On Off Off SR12 24x2k bal. On Off On SR12 24x2k On On Off DIP 4 Selects Multiplexing - On sets whole rack for MUX. (See Article S5Q-W1M...
-
Dial in test number, press RESET. Third digit adjusts test speed. Test # Function 800 Switch Test 810 Chase 820 Fade All 830 Fade One Output 840 One Output to Full 850 All Outputs to Percent