Question: What are the Fuse Changes for a Delta CEM? Answer: CEMD (120V Delta CEM) F2 changes from 1/8 Amp to 1/2 Amp. HCEMD (240V Delta CEM) F2 changes from a 1/8A. to 1/2 A. F3 changes from a 2A. to a 1A.
-
Sensor Backup Station (SBS) Pinout Pin Signal 1 12Vdc 2 GND 3 ETCLink Data - 4 ETCLink Data + This same pinout is also used for DAS stations.
-
Question: How Do I Wire and Use CEM Panic? Answer: CEM Panic is a contact closure which is wired to the CEM backplane in a Sensor rack. When the contact is closed, all dimmers which have been recorded into the Panic look are brought to full. Note that in multi-rack systems, the Panic switch is wired...
-
Problem: CEM displays Illegal Scale Error Message. Answer: Cause Can be the result of some corruption in the config, but does not impede system operation. Seems to be prevalent in large linked systems or CUDI systems Workaround / Fix There are many things that can make the message go away, but none of...
-
Question: How do I terminate ETCLink on a Sensor backup station? Answer: Insert jumpers on J5 A and B
-
Question: I did a rack to rack transfer on one CEM in my system. Now the rest of the CEMs say CONFIG MISMATCH. What did I do wrong? Answer: Sometimes in multi-rack system when you do a rack to rack transfer; once that is complete the rest of the CEMs in the system think there is a new config on the CEM...
-
Question: Where do I find the test switch on my CEM? Answer: It is the red switch on the PCB just behind the Keypad of the front panel.
-
How much power does a CEM Classic use? 0.1A Peak 0.09A Normal/Idle
-
Sensor CEM version 2 code does not have an "always on" firing mode but we can set a dimmer that way. To set a dimmer to be always on: Press [Setup] Press [1] for Dimmer Type the dimmer number on the numeric keypad and press [Enter] Press [4] to select Switched firing mode and press [Enter]...
-
When equipment goes bad out in the field, it's often extremely helpful if the owner/end user can keep track of the circumstances of the failure. This is especially true when the problem is intermittent and might not occur when the technician is present. Service Technicians are exceptionally skillful...
Posted to
ETC Product Wiki
by
Kelsey Aleckson
on
08-24-2009
Filed under: AAS, Acclaim, arri, ASTS, AVAB, CEM, CEM+, Congo, CongoJr, cRRFU, DAS, Dimmer, Distribution, DMX, ECMUX, Element, ELTS, Emphasis, Eos, ETCLink, Ethernet, Express, Expression, GCE, Idea, Ion, Irideon, K96, KnowledgeBase, Legacy Unison, LMI, Lon, MDD, MDR, MicroII, MicroVision, MIDI, MPE, NCE, Net2, Net3, Obsession, ObsessionII, Pharos, RDM, Response, RFR, RFU, RRFU, RS-232, RVI, Sensor, Sensor+, SineWave, SmartBar, SmartFade, SmartFadeML, SmartModule, SMPTE, Source Four, Source4, Touchscreen, Unison, Vision, WRFU