Module Information Summary This summary provides module information broken down by market and application. Four major market groups are used to separate modules: UL market – ETC Americas, 120V-60Hz power, Sensor and Unison products CE market – ETC Europe, 230V 50Hz power, Sensor CE and Unison...
-
The Socapex connector that is used by ETC: Socapex SL61 419AR The pinout for this is: CONNECTION CABLE CORE No. 1 Circuit 1 Live 2 Circuit 1 Neutral 3 Circuit 2 Live 4 Circuit 2 Neutral 5 Circuit 3 Live 6 Circuit 3 Neutral 7 Circuit 4 Live 8 Circuit 4 Neutral 9 Circuit 5 Live 10 Circuit 5 Neutral 11...
-
Manuals Sensor+ CEM+ v3.1.0 User/Configuration Manual Sensor+ CEM+ v3.0.0 User/Configuration Manual Sensor+ CE Installation Manual Sensor CEM Configuration Manual v1.0.2 Sensor CEM Configuration Manual v1.2.0 Sensor CEM Configuration Manual v2.0.0 Sensor CEM Configuration Manual v2.2.0 Sensor CEM Configuration...
-
For instructions about how to use Sensor3 Power Control system specific to CEM3 operation, terms, and definitions, also see CEM3 Power Control page. Sensor3 is the foundation for a versatile power system that builds on our proven Sensor workhorse system with CEM3 control. Sensor3 is coming soon to installation...
-
Question How Do I Clear Overtemp and Airflow (and other) Errors On The Sensor CEM? Answer Several of the errors that are considered to be critical to the well-being of the Sensor rack continue to display after error status is no longer present. These are referred to informally as "sticky" errors...
-
Question: Seeing flickering in a rack. Could this be due to an airflow problem? Answer: Yes it can. The rack can get caught between system ok and airflow error. This can cause flicker. If all of the dimmers that are active in the rack always flicker out together, airflow could be a factor. If they change...
-
There are a number of issues that can appear as "flickering" in a Sensor dimmer rack. Airflow issues are a common reason that all dimmers in a rack might flicker together: Sensor Dimmer Rack Flickering Due to Airflow Issues DMX problems might cause all dimmers in all racks to flicker sporadically...
-
In non-dimmed applications, branch circuits are often installed with three circuits sharing a common neutral conductor, where each of the three circuits is on a different phase. This is known as a “multiwire” branch circuit arrangement. It is used to save costs because only four total conductors...
-
Manuals Sensor CEM v3.1 User Manual 8867.Sensor CEM User Manual RevA 2000.pdf 8865.Sensor CEM User Manual v1.3.0 1997.pdf 2117.Sensor CEM User Manual v2.0.4 1994.pdf 8461.Sensor CEM User Manual v2.1.4 1996.pdf 3175.Sensor CEM User Manual v2.1.4 1996.pdf 7206.Sensor CEM User Manual v3.0.0 1998.pdf 2117...
-
Verify that the Max Scale setting for each dimmer on the CEM+ is set to about 118. Verify that the Curve setting for each dimmer on the CEM+ is set to Mod Square. If this doesn’t work, try Sensor 2.0. Make sure to check the voltage readings with a True-RMS meter. NOTE: Any work (including metering...