Source 4 HID Current Draw

Table of Contents

Page Details

First published by:
Kelsey Aleckson
on 07-23-2010
Last revision by:
Hans.Hinrichsen
on 01-07-2011
This page has not yet been rated

Source 4 HID Current Draw This page is locked to prevent further edits

Filed under: ,

Questions:

What is the current draw for HID fixtures?

What is the inrush current?

How many fixtures can I put on a circuit?

Answers:

HID inrush can draw upwards of 18-20 amps on a 120v service.  This inrush current only lasts for a very small fraction of a second.  Its duration is too short a time to trip breakers. 

The normal operating current draw for a 150W fixture is 1.4A at 120V and 1.85A for 277V.  A 70W fixture will draw .7A at 120V and .3A at 277V.

For a 20A breaker:

ETC's recommendation is no more than 10 150W HID instruments on a 20A, 120V service and no more than 15 150W instruments on a 20A, 277V service.   For 70W HID instruments, ETC recommends no more than 15 units on a 20A, 120V service, and no more than 20 units on a 20A, 277V service.

For a 15A breaker:

ETC's recommendation is no more than 7 150W HID instruments on a 15A, 120V service and no more than 10 150W instruments on a 20A, 277V service.   For 70W HID instruments, ETC recommends no more than 10 units on a 20A, 120V service, and no more than 15 units on a 20A, 277V service.

 

 