Filed under:

Engineering Notes
December 13, 1991

L86 Dimmer Modules BTU Dissipation

Heat dissipation in ETC dimmer racks is relatively simple to calculate. Use the following table to calculate either watts per dimmer or BTUs per dimmer, them multiply that number by the number of dimmers in the rack. Note that the watt and BTU figures shown below apply to single dimmer, not dimmer modules. (A module contains more than one dimmer)

L86-1200
24 watts/dimmer
82 BTUs/dimmer/hr
L86-2400
48 watts/dimmer
164 BTUs/dimmer/hr
L86-2400HR
100 watts/dimmer
341 BTUs/dimmer/hr
L86-6000
120 watts/dimmer
410 BTUs/dimmer/hr
L86-6000HR
250 watts/dimmer
854 BTUs/dimmer/hr

We suggest you set air conditioning levels to maintain the temperature in the dimer room at 68 degrees or less. ETC dimmers are designed to operate safely in environments with ambient temperatures of up to 104 degrees but, as with all electronics, keeping things cooler will help improve the service of the equipment.