<?xml-stylesheet type="text/xsl" href="http://www.etcconnect.com/Community/utility/FeedStylesheets/rss.xsl" media="screen"?><rss version="2.0" xmlns:dc="http://purl.org/dc/elements/1.1/"><channel><title>KnowledgeBase: Common Neutral Wiring in ETC Systems</title><link>http://www.etcconnect.com/Community/wikis/products/knowledgebase-common-neutral-wiring-in-etc-systems.aspx</link><description /><dc:language>en-US</dc:language><generator>CommunityServer 2008.5 SP1 (Build: 31106.3070)</generator><item><title>KnowledgeBase: Common Neutral Wiring in ETC Systems</title><link>http://www.etcconnect.com/Community/wikis/products/knowledgebase-common-neutral-wiring-in-etc-systems.aspx</link><pubDate>Tue, 04 Oct 2011 22:06:15 GMT</pubDate><guid isPermaLink="false">a7ac4d8e-197b-4214-ba03-8caf86a3094c:260</guid><dc:creator>Hans.Hinrichsen</dc:creator><comments>http://www.etcconnect.com/Community/wikis/products/knowledgebase-common-neutral-wiring-in-etc-systems/comments.aspx</comments><description>Current revision posted to ETC Product Wiki by Hans.Hinrichsen on 10/4/2011 5:06:15 PM&lt;br /&gt;
&lt;h2&gt;KnowledgeBase: Common Neutral Wiring in ETC Systems&lt;/h2&gt;
&lt;div style="font-size: 90%;"&gt;Filed under: KnowledgeBase, &lt;span style="text-decoration: line-through; color: red;"&gt;Sensor+&lt;/span&gt;&lt;span style="background: SpringGreen;"&gt;Legacy&lt;/span&gt; &lt;span style="background: SpringGreen;"&gt;Unison&lt;/span&gt;, Sensor, &lt;span style="text-decoration: line-through; color: red;"&gt;Legacy&lt;/span&gt; &lt;span style="text-decoration: line-through; color: red;"&gt;Unison&lt;/span&gt;&lt;span style="background: SpringGreen;"&gt;Sensor+&lt;/span&gt;, Unison&lt;/div&gt;

&lt;p&gt;In non-dimmed applications, branch circuits are often installed with three circuits sharing a common neutral conductor, where each of the three circuits is on a different phase. This is known as a &amp;ldquo;multiwire&amp;rdquo; branch circuit arrangement. It is used to save costs because only four total conductors (three hot, one neutral) are used to feed three branch circuits.&lt;/p&gt;
&lt;p&gt;This type of multi-wire branch circuit arrangement is not recommended for use with phase-control dimmers on new installations because it can cause voltage-drop interaction between the three branch circuits, as well as neutral conductor overloading.&lt;/p&gt;
&lt;p&gt;In a new development, the 2008 NEC section (210.4), adds a new condition requiring multiwire branch circuits to be fed from a multi-pole breaker, or three single-pole breakers with a handle-tie identified for the purpose. &lt;em&gt;This essentially eliminates new installations or retrofits using common neutrals on branch circuits fed from dimmer racks, because the handles of single-pole breakers in the dimmers cannot be mechanically tied together.&lt;/em&gt; The exact wording of the 2008 NEC is: &lt;/p&gt;
&lt;blockquote&gt;2008-210.4(B) &lt;strong&gt;Disconnecting Means.&lt;/strong&gt; Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.&lt;/blockquote&gt;
&lt;p&gt;&lt;strong&gt;&amp;nbsp;&lt;/strong&gt;&lt;/p&gt;
&lt;p&gt;&lt;strong&gt;If you have any questions about this information, please &lt;a class="ExistingPageLink" href="/Community/wikis/products/contact-etc-technical-services.aspx" title="Click to view the page titled: contact ETC Technical Services"&gt;contact ETC Technical Services&lt;/a&gt;.&lt;/strong&gt;&lt;/p&gt;</description></item><item><title>KnowledgeBase: Common Neutral Wiring in ETC Systems</title><link>http://www.etcconnect.com/Community/wikis/products/knowledgebase-common-neutral-wiring-in-etc-systems/revision/3.aspx</link><pubDate>Wed, 22 Jul 2009 20:53:27 GMT</pubDate><guid isPermaLink="false">a7ac4d8e-197b-4214-ba03-8caf86a3094c:6658</guid><dc:creator>Kelsey Aleckson</dc:creator><comments>http://www.etcconnect.com/Community/wikis/products/knowledgebase-common-neutral-wiring-in-etc-systems/comments.aspx</comments><description>Revision 3 posted to ETC Product Wiki by Kelsey Aleckson on 7/22/2009 3:53:27 PM&lt;br /&gt;
&lt;h2&gt;KnowledgeBase: Common Neutral Wiring in ETC Systems&lt;/h2&gt;
&lt;div style="font-size: 90%;"&gt;Filed under: KnowledgeBase, Sensor+, Sensor&lt;span style="background: SpringGreen;"&gt;,&lt;/span&gt; &lt;span style="background: SpringGreen;"&gt;Legacy&lt;/span&gt; &lt;span style="background: SpringGreen;"&gt;Unison&lt;/span&gt;&lt;span style="background: SpringGreen;"&gt;,&lt;/span&gt; &lt;span style="background: SpringGreen;"&gt;Unison&lt;/span&gt;&lt;/div&gt;

&lt;p&gt;In non-dimmed applications, branch circuits are often installed with three circuits sharing a common neutral conductor, where each of the three circuits is on a different phase. This is known as a &amp;ldquo;multiwire&amp;rdquo; branch circuit arrangement. It is used to save costs because only four total conductors (three hot, one neutral) are used to feed three branch circuits.&lt;/p&gt;
&lt;p&gt;This type of multi-wire branch circuit arrangement is not recommended for use with phase-control dimmers on new installations because it can cause voltage-drop interaction between the three branch circuits, as well as neutral conductor overloading.&lt;/p&gt;
&lt;p&gt;In a new development, the 2008 NEC section (210.4), adds a new condition requiring multiwire branch circuits to be fed from a multi-pole breaker, or three single-pole breakers with a handle-tie identified for the purpose. &lt;em&gt;This essentially eliminates new installations or retrofits using common neutrals on branch circuits fed from dimmer racks, because the handles of single-pole breakers in the dimmers cannot be mechanically tied together.&lt;/em&gt; The exact wording of the 2008 NEC is: &lt;/p&gt;
&lt;blockquote&gt;2008-210.4(B) &lt;b&gt;Disconnecting Means.&lt;/b&gt; Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.&lt;/blockquote&gt;
&lt;p&gt;&lt;strong&gt;&amp;nbsp;&lt;/strong&gt;&lt;/p&gt;
&lt;p&gt;&lt;strong&gt;If you have any questions about this information, please contact ETC Technical Services.&lt;/strong&gt;&lt;/p&gt;</description></item><item><title>KnowledgeBase: Common Neutral Wiring in ETC Systems</title><link>http://www.etcconnect.com/Community/wikis/products/knowledgebase-common-neutral-wiring-in-etc-systems/revision/2.aspx</link><pubDate>Thu, 16 Jul 2009 13:58:54 GMT</pubDate><guid isPermaLink="false">a7ac4d8e-197b-4214-ba03-8caf86a3094c:2019</guid><dc:creator>Kelsey Aleckson</dc:creator><comments>http://www.etcconnect.com/Community/wikis/products/knowledgebase-common-neutral-wiring-in-etc-systems/comments.aspx</comments><description>Revision 2 posted to ETC Product Wiki by Kelsey Aleckson on 7/16/2009 8:58:54 AM&lt;br /&gt;
&lt;h2&gt;KnowledgeBase: Common Neutral Wiring in ETC Systems&lt;/h2&gt;
&lt;div style="font-size: 90%;"&gt;Filed under: KnowledgeBase&lt;span style="background: SpringGreen;"&gt;,&lt;/span&gt; &lt;span style="background: SpringGreen;"&gt;Sensor+&lt;/span&gt;&lt;span style="background: SpringGreen;"&gt;,&lt;/span&gt; &lt;span style="background: SpringGreen;"&gt;Sensor&lt;/span&gt;&lt;/div&gt;

&lt;p&gt;In non-dimmed applications, branch circuits are often installed with three circuits sharing a common neutral conductor, where each of the three circuits is on a different phase. This is known as a &amp;ldquo;multiwire&amp;rdquo; branch circuit arrangement. It is used to save costs because only four total conductors (three hot, one neutral) are used to feed three branch circuits.&lt;/p&gt;
&lt;p&gt;This type of multi-wire branch circuit arrangement is not recommended for use with phase-control dimmers on new installations because it can cause voltage-drop interaction between the three branch circuits, as well as neutral conductor overloading.&lt;/p&gt;
&lt;p&gt;In a new development, the 2008 NEC section (210.4), adds a new condition requiring multiwire branch circuits to be fed from a multi-pole breaker, or three single-pole breakers with a handle-tie identified for the purpose. &lt;em&gt;This essentially eliminates new installations or retrofits using common neutrals on branch circuits fed from dimmer racks, because the handles of single-pole breakers in the dimmers cannot be mechanically tied together.&lt;/em&gt; The exact wording of the 2008 NEC is: &lt;/p&gt;
&lt;blockquote&gt;2008-210.4(B) &lt;b&gt;Disconnecting Means.&lt;/b&gt; Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.&lt;/blockquote&gt;
&lt;p&gt;&lt;strong&gt;&amp;nbsp;&lt;/strong&gt;&lt;/p&gt;
&lt;p&gt;&lt;strong&gt;If you have any questions about this information, please contact ETC Technical Services.&lt;/strong&gt;&lt;/p&gt;</description></item><item><title>KnowledgeBase: Common Neutral Wiring in ETC Systems</title><link>http://www.etcconnect.com/Community/wikis/products/knowledgebase-common-neutral-wiring-in-etc-systems/revision/1.aspx</link><pubDate>Fri, 19 Jun 2009 19:45:17 GMT</pubDate><guid isPermaLink="false">a7ac4d8e-197b-4214-ba03-8caf86a3094c:1827</guid><dc:creator>Kelsey Aleckson</dc:creator><comments>http://www.etcconnect.com/Community/wikis/products/knowledgebase-common-neutral-wiring-in-etc-systems/comments.aspx</comments><description>Revision 1 posted to ETC Product Wiki by Kelsey Aleckson on 6/19/2009 2:45:17 PM&lt;br /&gt;
&lt;p&gt;In non-dimmed applications, branch circuits are often installed with three circuits sharing a common neutral conductor, where each of the three circuits is on a different phase. This is known as a &amp;ldquo;multiwire&amp;rdquo; branch circuit arrangement. It is used to save costs because only four total conductors (three hot, one neutral) are used to feed three branch circuits.&lt;/p&gt;
&lt;p&gt;This type of multi-wire branch circuit arrangement is not recommended for use with phase-control dimmers on new installations because it can cause voltage-drop interaction between the three branch circuits, as well as neutral conductor overloading.&lt;/p&gt;
&lt;p&gt;In a new development, the 2008 NEC section (210.4), adds a new condition requiring multiwire branch circuits to be fed from a multi-pole breaker, or three single-pole breakers with a handle-tie identified for the purpose. &lt;em&gt;This essentially eliminates new installations or retrofits using common neutrals on branch circuits fed from dimmer racks, because the handles of single-pole breakers in the dimmers cannot be mechanically tied together.&lt;/em&gt; The exact wording of the 2008 NEC is: &lt;/p&gt;
&lt;blockquote&gt;2008-210.4(B) &lt;b&gt;Disconnecting Means.&lt;/b&gt; Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.&lt;/blockquote&gt;
&lt;p&gt;&lt;strong&gt;&amp;nbsp;&lt;/strong&gt;&lt;/p&gt;
&lt;p&gt;&lt;strong&gt;If you have any questions about this information, please contact ETC Technical Services.&lt;/strong&gt;&lt;/p&gt;</description></item></channel></rss>